Can I use a metal building that is bonded at one side where the panel is and bond the gas line at the other side? Or do I have to run a separate piece of copper 150 ft ?
as I understand things, you don't normally have to make any special bond to a regular gas line. the egc is adequate.Can I use a metal building that is bonded at one side where the panel is and bond the gas line at the other side? Or do I have to run a separate piece of copper 150 ft ?
Thank youas I understand things, you don't normally have to make any special bond to a regular gas line. the egc is adequate.
if you need to make a bond to csst though, you have to make it from the grounding electrode system to where ever the gas line enters the building. I don't believe the building steel can be used as part of this bonding connection.
Is the building steel being used as electrode and part of the electrode system.Can I use a metal building that is bonded at one side where the panel is and bond the gas line at the other side? Or do I have to run a separate piece of copper 150 ft ?
If it is csst the bond is supposed to reduce the risk of pinholes developing from nearby lightning strikes. I gather there is a type of csst that is now made that is not susceptible to this problem.What size conductor would be used on a gas line bond as it cannot be used as a GE so would bonding wire only be required to be sized to that which could possibly energize it, not the GEC?
That takes care of the appliance side of the CSST, which is why bonding the source side effectively bypasses the CSST.Otherwise, the circuit egc that accompanies whatever might energize a gas line is adequate for clearing faults.
It should be sized by 250.122 based on the OCPD for the circuit 'likely to energize' the piping. See 250.104(B), 2020 NEC reference.What size conductor would be used on a gas line bond as it cannot be used as a GE so would bonding wire only be required to be sized to that which could possibly energize it, not the GEC?
#6 cu is the only size I've ever used or heard of.What size conductor would be used on a gas line bond as it cannot be used as a GE so would bonding wire only be required to be sized to that which could possibly energize it, not the GEC?
Probably because 250.104 requires you to follow 250.64(B). And also #6 meets for 250.122 for the worst case scenario on a 200A service.#6 cu is the only size I've ever used or heard of.