I have been studying for Wa state 01 admin test, I failed it the first time. I have been reading all the threads here for info. My question is this: Since a duplex is not considered a multifamily dwelling when you do the standard load calc do you double the small appliance and laundry circuit or do you just count it once, like the 25% for the largest motor?
 

Smart $

Esteemed Member
Location
Ohio
Small appliance loads are 2 minimum per unit, period... doesn't matter how many units.

Laundry is always 1 minimum in one-family dwellings. In two- or multi-family dwellings it's either 1 minimum, or none, per unit. On the surface, that doesn't make much sense :roll::cool:. Refer to the exceptions of 210.52(F)...
 
Last edited:

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
The thing you need to watch carefully, as you read the test questions, is whether they are asking you to size the feeder to a single unit, or whether they are asking you to size the service to the duplex as a whole. Those are separate calculations, and you might be asked for both answers.

For a single unit's feeder, you account for 2 SA circuits, and that 3,000 VA is what goes into the demand factors of Table 220.42. For the service to the duplex, you account for 4 SA circuits, and the total of 6,000 VA is inclulded in what you use, when you look at Table 220.42.

Good luck with the test. I failed my first time as well, but passed the second time (over 8 years ago).
 
thanks for the input

thanks for the input

Thanks for the input. I wish I had found this forum before I took it the first time. I actually have taken it twice but the second time the computer froze up on me and I got to reschedule. Both tests (10 questions each) had 2 questions on each of them, probably because they fall in a somewhat ambiguous area. I have found similar if not exact questions on this forum but most of them were not done right. Never the less they have helped me in this area. I have Mike Holts and the other guys books (Tom H) and both of them miss this particular calculation.
 