We have ran into a situation of the following and I can't come up with an answer, but I came up with a number of possibles. So, I present to the forum the following. " Switched outlet lets say, no further than 30ft from the wall switch on the longest situation and 15ft on the other situation same problem separate rooms switchs and outlets. " Final on a home, When the gfci polarity tester is plugged into the switched half, the open equipment grounding conductor light is slightly illumintated. When you read from the red wire (switched conductor) the voltage, with the switch in the o-f-f position, to neutral (white conductor) the voltmeter reads between 14 volts on the short run and 40 volts on the long run. The three wire was replaced with a new 3 wire laying in the room and the results were the same.
a) I suspected at first, a tight staple.b) a roll of nmb that had received a drowning c) maybe a loose grounding electrode conductor or a loose neutral in the panel (neither one are apparent).
Your turn? Thanks.
a) I suspected at first, a tight staple.b) a roll of nmb that had received a drowning c) maybe a loose grounding electrode conductor or a loose neutral in the panel (neither one are apparent).
Your turn? Thanks.