I have a sauna that is about 100’ from power source, it is 25a 240v I’m using #10 THHN, my question is can I use a #12 ground?
So what size did you come up with?Disregard, I found my answer. Thanks
EGC size no require larger than circuit conductor size 250.122AOther factors might require you to use an even larger ground,
Correct, but if you use a 1/0 circuit conductor for a 15 amp circuit, the EGC is required to be 1/0.EGC size no require larger than circuit conductor size 250.122A
EGC size no require larger than circuit conductor size 250.122A
Parallel conductors case?few corner cases where the allowed phase conductors may be smaller than table 250.122
250.122A still apply. EGC size need no exceed 12awgI was thinking motor or HVAC loads where you might see a 30A breaker protecting 12 ga conductors
Sort of. The EGC may be required to be larger than the individual parallel phase conductors.Parallel conductors case?
250.122A still apply. EGC size need no exceed 12awg
I didn't know that. I assumed the smaller taps were enough to trip the breaker then the smaller equipment grounding conductor would also work.Also the EGC for tap conductors is based on the OCPD ahead of the tap so that EGC may be required to be larger than the tap conductors.
Agreement by experts like you joyful momentsI'm not arguing with you. I pointed out the general table, you pointed out the exception to the table, I agreed with you. You asked if I was thinking about large parallel installations, I said I was thinking about motor and HVAC installations.