Re: I have a sicheation about converting a three phase panel
there's nothin wrong with that, it might be a pain though cuz if its 30 pole, 1/3rd of the poles will not be energized.
I don't think he is allowed to put a jumper to tie in two lugs, because those lugs have ampacity ratings, and he might overload the connection, plus that would unbalance your phases and you would be carrying current in your neutral and wasting energy.
I think he wants to do this, he should leave one phase of the 3 phase panel unenergized and leave the punch outs on the panel face in for breakers that would fit in the unenergized slots, or put spare breakers in those slots with no connections to them, and mark them accordingly.
[ July 30, 2003, 10:23 AM: Message edited by: bonding jumper ]