I HAVE 4 LOADS ON A 3 PHASE WYE CONNECTED ELECTRIC SERVICE. 3/ 15KW CONTINUOUS LIGHTING LOADS.AND ONE 30KW CONTINUOUS HEATER LOAD WHAT IS THE ALLOWABLE AMPACITY OF THESE LOADS. I DO NOT KNOW THE STEPS TO ANSWER THIS PLEASE HELP ME I AM THANKFULL FOR THIS SITE AND EVERYONE IS VERRY HELPFULL Sorry for the misleading info its a 208/120v wye and the heater is 3 phase

[ July 10, 2004, 01:59 PM: Message edited by: littlerich ]
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: I HAVE ANOTHER QUESTION

Rich, please turn off your caps. You haven't provided enough information for the question to be answered.

I would assume the lighting is phase to neutral loads, but what is the voltage?

Is the water heater single phase or three phase and once again what is the system voltage?

Is the question really asking for "Allowable" ampacity?

Roger
 

chris68

Member
Location
Denver, CO
Re: I HAVE ANOTHER QUESTION

Continuous ampacity = 125 percent. Need to know the voltage.

[ July 11, 2004, 12:35 AM: Message edited by: chris68 ]
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: I HAVE ANOTHER QUESTION

First, your use of the phrase ?allowable ampacity? does not make sense here. Are you asking for the size of conductor that you need to install, as a minimum, in order to be able to handle these four loads, presuming that there are no other loads? Or are you asking what the actual current will be from these four loads? Or are you asking how much current you need to take into account, when counting these loads as part of an overall service calculation? What, in short, is the purpose for which you are performing this calculation?

Let me assume that the lighting loads are 120 volts, and that the three lighting loads are installed in a balanced way over the three phases of the supply. You have clarified that the heater is 3-phase, so I infer it is rated at 208 volts. You start any such calculation by adding the power, not the current. That part is easy: 15 + 15 + 15 + 30 = 75 KW. I believe we can treat these lighting and heating as purely resistive loads, and so state that the total load is 75KVA.

The current in any one phase would be 75 KVA divided by 208 volts and divided again by the square root of three. The common shortcut is to divide 75 KVA by 360, and get 208 amps (you can ignore the coincidence that it matches the voltage number). To figure the smallest conductor needed to serve these loads, multiply by 125% (since both lighting and heating have been declared to be continuous). You need a minimum of 260 amps worth of conductor. A 300 MCM THHN Copper would do the trick. As to service load calculations, you go back to the 75 KVA, and multiply by the 125%. These four loads add 93,750 to the service calculation. Please note, however, that the lights might have been taken into account in another part of the calculation, in the form of VA per square foot, so take care to avoid duplication.

Does this answer your question?
 