The following figure depicts a load side interconnection of a PV system via a 300 A breaker to a 1,200 A switchboard with a 1,200 A main breaker. Please indicate how this system meets or does not meet the requirements of NEC 705.12(B).
Have you read the section? It seems pretty clear in providing the information needed to answer the question. There is a second level subdivision for busbar.
Have you read the section? It seems pretty clear in providing the information needed to answer the question. There is a second level subdivision for busbar.
705.12(B)(1)The sum of 125 percent of the power source(s) output circuit current and the rating of the overcurrent device protecting the busbar shall not exceed the busbar ampere rating. Informational Note: This general rule assumes no limitation in the number of loads or sources applied to busbars or their locations.
or
705.12(B)(2)Where two sources, one a primary power source and the other another power source, are located at opposite ends of a busbar that contains loads, the sum of 125 percent of the power-source(s) output circuit current and the rating of the overcurrent device protecting the busbar shall not exceed 120 percent of the busbar ampere rating.
2023 NEC 705.12(B)(2) applies. Basically, the sum of the rating of the input breakers cannot exceed 120% of the bus rating. 1200A (MCB) + 300A (PV CB) is greater than 1200A*1.2, so the installation does not meet the requirement.