I believe I know the answer to this but considering it is being used in a multi family dwelling (36 units total) I would like a second opinion.
We are running circuits for condensers. Using NM for the circuits. The condenser is:
Min circ: 16.4
Max brkr 20
Since 14 is good for 20 amp in the 60degree column I told the guys to use it. I know 240.4 is not used in this situation since we would use 440 but can someone just please agree with me.
Everyone has that fear of a 20amp breaker on 14 wire.