I had a similar experience with an old portable concrete plant, they called and said the it just wouldn't do anything, found the control fuse blown right off, replaced it, still wouldn't run. They pulled out three different sets of prints on it and said it was wired by all three over the years. This plant was so old, there was no PLC's, everything ran off of a clock motor turning a cam with about 30 micro switches attached to it. About 30 minutes into troubleshooting it, I found the e-stop circuit was open, all of the e-stops were manually activated, but none was pushed. After telling the maintaince man there was an open in the e-stop circuit, he said "Oh, yea, I replaced the contact on that one over there this morning. He had replaced a normally closed contact with a normally open, not knowing there was a difference!