Today was the perfect end to the week!

Get up and it's 55? out. Sun is rising. Jump in the truck, and head to the supply house. Pick up some #2 ACSR and wedge clamps, and stop and pick up a lift.

Service call for the day: HO had a short in the line 'twixt the pole and the house. He managed to locate it at one of the lowest points on the drop, so he installed a temporary fix. So I went out and replaced the line today.

DSC_3339a.jpg


Yea, that's me up there!



DSC_3368a.jpg


DSC_3361a.jpg




HO's temp fix:

DSC_3362a.jpg



I'm not a big fan of linework, but little things like this I love......... fresh air.... sunshine..... out in the middle of nowhere...... working alone and doing my thing.................. and getting high!
 

iwire

Moderator
Staff member
Location
Massachusetts
Interesting, here that would be POCO work, if it's not POCO work and covered by the NEC ASCR is not a legal conductor.
 

iwire

Moderator
Staff member
Location
Massachusetts
Interesting point. I had not considered that the triplex cable is not covered by the NEC,

Unless it is some sort if dual listed product it will not be UL listed and it will not be in Table 310.13 so you can't use it.


but what could you use to do this job? :wink:

I would tell the customer to call the POCO for a free repair. :D
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Interesting, here that would be POCO work, if it's not POCO work and covered by the NEC ASCR is not a legal conductor.

Same here.
From the meter in on laterals and from the top of the house on overheads is the owners.
 

hurk27

Senior Member
It seems this is the description of ASCR cable to me?

396.2 Definition.
Messenger Supported Wiring. An exposed wiring support system using a messenger wire to support insulated conductors by any one of the following:
(1) A messenger with rings and saddles for conductor support
(2) A messenger with a field-installed lashing material for conductor support
(3) Factory-assembled aerial cable
(4) Multiplex cables utilizing a bare conductor, factory assembled and twisted with one or more insulated conductors, such as duplex, triplex, or quadruplex type of construction

And this is in table 396.10(A)
Other factory-assembled, multiconductor control, signal, or power cables that are identified for the use
Note that this is the only cable in this table that doesn't have an article listed for reference?
 

mivey

Senior Member
Looks like these folks go without electricity. :wink:
Are you saying you have never done work that was covered by the NESC, say ahead of the service point...like something that the utility required the customer to install? Wouldn't that qualify as "not POCO work and not covered by the NEC"?
 

hurk27

Senior Member
To me this looks like a common farm type service, with the metering at the pole by the garage and feeders feeding the different loads by aerial cable?

We have a few of these around here on farms
 