i might be imaing things but.....

Status
Not open for further replies.

nafis

Senior Member
Location
Palestine,tx
I was flipping through the electrical contractor magazine, I notice on page 33 HD has picture with j. box. I think the wire in the JB picture did not comply with the 6? rule. not sure of the code number . I knew its just a picture but can any body tell me what?s the code number please.

Thank you
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What month is that issue?

300.14 Length of Free Conductors at Outlets, Junctions, and Switch Points.
At least 150 mm (6 in.) of free conductor, measured from the point in the box where it emerges from its raceway or cable sheath, shall be left at each outlet, junction, and switch point for splices or the connection of luminaires or devices. Where the opening to an outlet, junction, or switch point is less than 200 mm (8 in.) in any dimension, each conductor shall be long enough to extend at least 75 mm (3 in.) outside the opening.
Exception: Conductors that are not spliced or terminated at the outlet, junction, or switch point shall not be required to comply with 300.14.
 