qopanel
Member
- Location
- NW Chicago Burbs
Here is my situation. I am installing a back up generator for a lift station and, the building it sits in has NO steel or water. The footings and foundation were poured before I had the contract, and the floor will have no rebar and has to have a plastic vapor barrier installed over 6" of gravel. The electrical inspector I talked to 4 weeks ago told me to give him a call, and he would walk me though what he wanted for grounding. I called him today to meet me on site, only to find out that he has left, and the City has no electrical inspector to replace him. The print is very genaric and shows no real grounding details. I'm total lost with no steel or water.
Here is the order of the electrical equipment I'm installing.
3phase 480v 200amp meter socket outside. 2 ground rods driven.
70amp fused nema 3r service rated disconnect, mounted next to meter outside.
3pole auto Transfer switch. ( non switched noodle )
480volt 70amp main panel board. Total load 43 amps
15kva transformer.
120/208volt 40amp panel board.
40kva 3phase 480volt generator to back up entire load ( 43amps ) ( I know not to bond the neutral here ).
What should be bonded?
Do I drive a ground rod at the transformer?
Do I need any others?
Should I just use a common EGC for the entire system?
I'M SOOOO LOST......
Here is the order of the electrical equipment I'm installing.
3phase 480v 200amp meter socket outside. 2 ground rods driven.
70amp fused nema 3r service rated disconnect, mounted next to meter outside.
3pole auto Transfer switch. ( non switched noodle )
480volt 70amp main panel board. Total load 43 amps
15kva transformer.
120/208volt 40amp panel board.
40kva 3phase 480volt generator to back up entire load ( 43amps ) ( I know not to bond the neutral here ).
What should be bonded?
Do I drive a ground rod at the transformer?
Do I need any others?
Should I just use a common EGC for the entire system?
I'M SOOOO LOST......