I am designing a restaurant that's within a large mixed use building. Our equipment is connecting to a retail service through that's fed from a main switchboard (MCS1). I have the base building drawings that include an arc fault riser diagram, but I am having trouble understanding how to best utilize it for selecting my equipment.
The main switchboard has an fault current of 150.4 kA. Our 400A CT cabinet, meter, and main disconnect will tie into the through coming off this switchboard. From there, it will be around 200 feet of cable to a 400A panel within out tenant space.
I know i need to size the AIC rating of my equipment to be equal or exceed the fault current available on the line side of the terminals. Should i assume that the available fault current at the terminals will be approximately 150 kA? or will there be significant losses along the way? I thought typically panels have AIC rating of 22k-65k.
Thank you for any feedback.
The main switchboard has an fault current of 150.4 kA. Our 400A CT cabinet, meter, and main disconnect will tie into the through coming off this switchboard. From there, it will be around 200 feet of cable to a 400A panel within out tenant space.
I know i need to size the AIC rating of my equipment to be equal or exceed the fault current available on the line side of the terminals. Should i assume that the available fault current at the terminals will be approximately 150 kA? or will there be significant losses along the way? I thought typically panels have AIC rating of 22k-65k.