Hi everyone. We are installing two 2000 amp aluminum electrical busway (480Y) systems that will be feed from one 2500 kVa transformers. The busway taps all have over current protection that we have sized to allow a maximum amperage capacity of 1400 amps to ever travel though the busway. Between the transformer and the busway we of course need to have proper over current protection.We are looking at feeding two disconnects rather than large distribution gear since the disconnects are smaller and can be installed indoors for ease of access in case of an emergency.
I'm not fully educated as to how to properly size the disconnects and I need a bit of help. Essentially, the 600v rating is the only confusing part for me. A 1200 amp 600v disconnect is a common size, whereas a 1600 amp seems to be a custom and/or expensive unit. Mathematically speaking, we are running a maximum load of ~1,164 kVa. 1200 amp @ 600v gives a mathematical maximum load of ~1,247 kVa. Of course we are running 480v though the system, but does the fact that the gear rating is 600v change the sizing calculation?
I'm not fully educated as to how to properly size the disconnects and I need a bit of help. Essentially, the 600v rating is the only confusing part for me. A 1200 amp 600v disconnect is a common size, whereas a 1600 amp seems to be a custom and/or expensive unit. Mathematically speaking, we are running a maximum load of ~1,164 kVa. 1200 amp @ 600v gives a mathematical maximum load of ~1,247 kVa. Of course we are running 480v though the system, but does the fact that the gear rating is 600v change the sizing calculation?