this i a correction i am dealing with .
we have a heat pump with a MCA 21 max OCP 25 .
I ran #12 THHN and put it on a 25 amp breaker. The following is what he stated when i questioned the correction. if im wrong could somebody please educate me here.
While Table 310.16’s ampacities are pretty much as you stated, the limitations we must comply with are the foot notes to the table identified by the asterisk (*) that appears next to the conductor sizes on the left. Here we read that #10 is to be protected at 30 amps, #12 is to be protected at 20 amps and #14 is to be protected at 15 Amps
Since your min ckt ampacity is (if I recall correctly) around 21 amps and your MOCP is 25 Amps as listed on the unit’s label you sized the OCP correctly. However, this places your #12 conductors over the 20 Amp OCP stated on the table footnote. Your will need to install #10 Cu to replace the #12.
we have a heat pump with a MCA 21 max OCP 25 .
I ran #12 THHN and put it on a 25 amp breaker. The following is what he stated when i questioned the correction. if im wrong could somebody please educate me here.
While Table 310.16’s ampacities are pretty much as you stated, the limitations we must comply with are the foot notes to the table identified by the asterisk (*) that appears next to the conductor sizes on the left. Here we read that #10 is to be protected at 30 amps, #12 is to be protected at 20 amps and #14 is to be protected at 15 Amps
Since your min ckt ampacity is (if I recall correctly) around 21 amps and your MOCP is 25 Amps as listed on the unit’s label you sized the OCP correctly. However, this places your #12 conductors over the 20 Amp OCP stated on the table footnote. Your will need to install #10 Cu to replace the #12.