This is at a Hospital..maybe I am just use to Hospital regualtions but here goes....
A new 3000 amp Switchboard is being installed in a new part of the hospital.
Existing Utility Transformer (13.8 to 480 volt 3 Phase) will be relocated and will feed this new 3000 amp Switchboard.
New 3000 amp Switchboard will have a 1600 amp breaker in it to feed the existing Switchboard by way of running new conduits to the old Utility Transformer Pad, installing a junction box and capturing the old conduits that fed existing Switchboard. These conduit only have 4 conductors in them... 3-500 mcm (A,B,C) and one 4/0 Neutral... No Ground Conductor.
I was under the impression that all conduits were going to be repulled with new wire and a Ground would be added. Electrical contractor wants to reuse the existing conductors from junction box to the existing Switchboard. Does this meet Code?
This existing Switchboard is now going to be a big Sub panel in my opinion and its Ground should originate from the new Switchboard. The existing Neutral to Ground Bar Bonding Jumper at existing Switchboard needs to be removed.
Am i missing an exception in the Code? Any input is appreciated.
Thanks
Shortckt
A new 3000 amp Switchboard is being installed in a new part of the hospital.
Existing Utility Transformer (13.8 to 480 volt 3 Phase) will be relocated and will feed this new 3000 amp Switchboard.
New 3000 amp Switchboard will have a 1600 amp breaker in it to feed the existing Switchboard by way of running new conduits to the old Utility Transformer Pad, installing a junction box and capturing the old conduits that fed existing Switchboard. These conduit only have 4 conductors in them... 3-500 mcm (A,B,C) and one 4/0 Neutral... No Ground Conductor.
I was under the impression that all conduits were going to be repulled with new wire and a Ground would be added. Electrical contractor wants to reuse the existing conductors from junction box to the existing Switchboard. Does this meet Code?
This existing Switchboard is now going to be a big Sub panel in my opinion and its Ground should originate from the new Switchboard. The existing Neutral to Ground Bar Bonding Jumper at existing Switchboard needs to be removed.
Am i missing an exception in the Code? Any input is appreciated.