I should know this but...

Status
Not open for further replies.

laketime

Senior Member
I am sizing the feeders for a 200amp residential load center off a meter. I am figuring 2/0 for the feeders (Table 310.15(B)(6)) and a #4 for the ground (Table 250.66). Is that correct? Also what section do I use for the grounding conductor from the panel to the ground rod? We are using the 2008 code. I know the NEC does not require a ground from the meter to the load center, but I have been told that the local inspectors don't see it that way and just pull the ground and drive another rod by the load center location. Comments and questions welcomed.
 

JES2727

Senior Member
Location
NJ
Look at Table 250.66 to size your grounding electrode conductor, and Table 250.122 for your equipment grounding conductor.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
I know the NEC does not require a ground from the meter to the load center, but I have been told that the local inspectors don't see it that way

We buy meterbases with the neutral lug already bonded to the can. Cooper B-Line is one type.
 