mbrooke
Batteries Included
- Location
- United States
- Occupation
- Technician
Why do health care facilities almost always have only one generator branch running to critical care areas? Why do so many older facilities lack normal branch power in OR, ERs and ICUs?
And appearing to be more out of design rather than capitol economics?
Case in point: ~ 1.2 million square foot hospital. 2 600kw and 1 400kw generator. One critical branch, one none bypass ATS, generator maintenance leaves critical branch without backup power and both normal/critical branches originate from the same unit substation bus section despite several substations/multiple MV utility feeds being present in the same building. The other two generators feed elevators, chillers, imaging, servers, boilers, ect but no life support equipment. Elevators have a manual transfer switch downstream to allow for service of the automatic one.




Case in point: ~ 1.2 million square foot hospital. 2 600kw and 1 400kw generator. One critical branch, one none bypass ATS, generator maintenance leaves critical branch without backup power and both normal/critical branches originate from the same unit substation bus section despite several substations/multiple MV utility feeds being present in the same building. The other two generators feed elevators, chillers, imaging, servers, boilers, ect but no life support equipment. Elevators have a manual transfer switch downstream to allow for service of the automatic one.