Ok, we have a 12amp continuous load in a 50'C ambient. What size MN-B to use?
12amp x 1.25 = 15amp, select #14 NM-B, 15amp OCPD and check for temp correction.
#14 in MN-B is THHN, 25amp in 90'C column.
25amp x 0.82 = 20.5amp
So we are OK w/ #14 NM-B protected at 15amp in a 50'C ambient.
Now please look here:
http://ecmweb.com/nec/code_quiz_072506/
He seems to be looking at this statement in 334.80
partial code quote)
.....provided the final derated ampacity does not exceed that for a 60'C (194'F) rated conductor.
I always took that to mean you cannot protect above the 60'C rated ampacity, and in the case of #14 we can't exceed 15amp per 240.4(D) anyway.
He seems to be saying you can't use it (#14NM-B) because your calc results in a number higher than the 60'C amps.
Please advise. This is pretty basic stuff. If I'm mistaken, I may need to change careers.
EDIT: I don't know why that frown is up there.
12amp x 1.25 = 15amp, select #14 NM-B, 15amp OCPD and check for temp correction.
#14 in MN-B is THHN, 25amp in 90'C column.
25amp x 0.82 = 20.5amp
So we are OK w/ #14 NM-B protected at 15amp in a 50'C ambient.
Now please look here:
http://ecmweb.com/nec/code_quiz_072506/
He seems to be looking at this statement in 334.80
.....provided the final derated ampacity does not exceed that for a 60'C (194'F) rated conductor.
I always took that to mean you cannot protect above the 60'C rated ampacity, and in the case of #14 we can't exceed 15amp per 240.4(D) anyway.
He seems to be saying you can't use it (#14NM-B) because your calc results in a number higher than the 60'C amps.
Please advise. This is pretty basic stuff. If I'm mistaken, I may need to change careers.
EDIT: I don't know why that frown is up there.