I used 1/2 inch rigid straps today

Status
Not open for further replies.

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
In my house to secure 2-2-2-4 aluminum cable today.
I asked for cable straps and that is what they gave me. Didn't notice till I got home. Worked great!
Knowing its a violation how many of us have used them for the same thing? ;:cool:
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
I don't see the violation. I use straps like that all the time for SER and larger NM cable.
Unless they are listed for use on that cable I would think thats the violation.
But then again maybe they don't have any listing for anything. But it was stamped right on the strap 1/2 rigid.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Unless they are listed for use on that cable I would think thats the violation.
But then again maybe they don't have any listing for anything. But it was stamped right on the strap 1/2 rigid.
Would you object to a service-cable staple used to secure PVC conduit?
 
Status
Not open for further replies.
Top