Long chat with the tech support guy at a name brand automation company this morning.
Long and short of it is a customer bought a switch rated for div 2 that ended up being installed in a div 1 area. Not a big deal, just add an IS barrier - right?
Tech support suggested a part number to customer for IS barrier. I look for wiring diagram. The only documentation they have shows it hooked to a Namur sensor, and nothing in the document says you can hook it to dry contacts.
Tech support says Namur is considered a simple device so you can use barrier with any simple device. I say - where does it say that in the manufacturers documentation. Tech support says - you can google simple device. I say - google is not manufacturer.
Am I being too an^l about the control drawing requirement?