Re: I wonder what this will cost to fix
It looks like a CT metering setup to me. The power doesn't go through the meter. Current Transformers (donuts) are placed around the transformer tabs or around the conductors (sometimes in a separate CT cabinet). The meter reads the CTs. It works kind of like clamp-on amp meters.
Depending on the voltages involved, there may also be PT's (potential transformers) that feed the meter, too.
If you remove the meter in a CT metering system, then the meter just stops measuring power consumption -- it doesn't shut off the power to the building.
CT metering is usually employed for services that are larger then 400 Amp. When you get into the 600A and larger entrances, they don't make meters or meter bases that will allow the full amperage to feed through them.
Edited to add: The red thing would be the meter socket that the meter plugs into. The plug-in fingers are much smaller because all that's going to the meter is curent and voltage from CTs and PTs. It looks like the meter is still stuck in the meter cover that is hanging loose. You're seeing the back side of the meter. The bent-up cover just needs to be replaced and the meter plugged back in if there's no other damage.
It also looks like the CT meter base is mounted on the front of another larger box, which is probably a CT enclosure. In that case, the CTs would be in the larger box and the entrance conductors would be run through the donut shaped CTs ( 1 ea. CT per phase & N) in that box. Looks like 1 large conduit in from the bottom -- and probably feeds out through the back through the wall to the service main disconnect???
[ August 18, 2005, 01:47 PM: Message edited by: tx2step ]