You guys have been helpful in the past, thanks. I'm trying to pass ICC electrical plan review exam and bought the IAEI study guide. So here's the question, I don't understand the answer explanation.
30. A service equipment is rated 208Y/120V, 3-phase. The busbars in the service equipment are rated 800 amperes. The calculated load is 675 amperes. The service disconnecting means consists of two 150-ampere, 3-pole; one 200-ampere, 3-pole; one 400-ampere, 3-pole; and one 300 ampere, 3 pole circuit breakers. The equipment is identified as suitable for service equipment. The service entrance conductors consist of four 400kcmil Type THW copper conductors in each of two metric designator 78 (trade size 3) rigid metal conduits. Which one of the following violations is applicable?
A. A single main disconnecting means is required
B. The ratings of the disconnecting means do not comply
C. The permitted conduit fill is exceeded
D. The service entrance conductors are undersized
The book says the answer is D. because 400kcmil CU is rated for 335 amperes. 335 amperes x (2) = 670 amperes which is less than the calculated load of 675 amperes, the conductors are undersized.
Would this not be 3 phase conductors in two parallel runs with each phase rated for 335 amperes which would be 2010 amps?? Thanks for helping me out on this one.
30. A service equipment is rated 208Y/120V, 3-phase. The busbars in the service equipment are rated 800 amperes. The calculated load is 675 amperes. The service disconnecting means consists of two 150-ampere, 3-pole; one 200-ampere, 3-pole; one 400-ampere, 3-pole; and one 300 ampere, 3 pole circuit breakers. The equipment is identified as suitable for service equipment. The service entrance conductors consist of four 400kcmil Type THW copper conductors in each of two metric designator 78 (trade size 3) rigid metal conduits. Which one of the following violations is applicable?
A. A single main disconnecting means is required
B. The ratings of the disconnecting means do not comply
C. The permitted conduit fill is exceeded
D. The service entrance conductors are undersized
The book says the answer is D. because 400kcmil CU is rated for 335 amperes. 335 amperes x (2) = 670 amperes which is less than the calculated load of 675 amperes, the conductors are undersized.
Would this not be 3 phase conductors in two parallel runs with each phase rated for 335 amperes which would be 2010 amps?? Thanks for helping me out on this one.