Thanks for all the previous help...here's another thing I'm confused about: Question # 46 pg. 92 -
A central heating and air conditioning unit has the following information on the name plate: Min. circuit ampacity 28 Amps, Max. fuse size 45 Amps. What is the minimum size Type THW conductor that may be used to supply this unit?
A. 12AWG
B. 10 AWG
C. 8 AWG
D. 6 AWG
Ok I get 28 amps x 1.25% = 35 amps. They say the correct answer is B. 10 AWG....I thought since it is 100 amps or less we have to use the 60deg C column? My answer would have been C. 8 AWG.