IBC 1006.3 Exterior emergency lighting and 2002 NEC 700

Status
Not open for further replies.

jaburch

Member
How have you been enforcing the connections for the required emergency lighting on the exterior of an exit discharge? NEC 700.12(E) says to connect to local circuit which is, in strip malls, the exterior soffit or wall pack circuit. This is tough in tenant improvements because the tenant must now connect to the Landlord's exterior circuit which often does not have an existing unswitched leg.
Also 700.16 says the space cannot be dark with one lamp failure. Emergency light fixtures at the exit would have to have two lamps if a solitary unit. Is night time exterior light contribution acceptable as assurance against total darkness?
 
Re: IBC 1006.3 Exterior emergency lighting and 2002 NEC 700

I have been using either 2 fixtures or a single dual lamp fixture for outside. You can get fluorescent packs and can lights with 2 lamps and an emergency battery.

I'm not sure connecting the emergency lighting to the local circuit was intended to cover outdoor lighting (but I've been wrong before :D ). I think the intent so that people don't all stop at the doorway when exiting a space that has lost power. If that is the intent, I think it is better to have the outdoor fixture connected to the same circuit that serves lighting in the store. Maybe your AHJ would approve this.
 