Re: ICC Code
Ron, that must be it.
I looked in mine, and I do not see how those sections state that they must be 120v.
1202.5
Smoke Detector Circuts.
Smoke detectors required by the
International Building Code and installed within dwelling units shall not be connected as the only load on a branch circut. Such detectors shall be supplied by branch circuts having lighting loads consisting of lighting outlets in habitable spaces.
1202.15
Smoke Alarm Power Source.
In new construction, required smoke alarms shall receive their primary power from the building wiring where such wiring is served from a commercial source and shall be equipped with a battery back-up. Smoke alarms shall emit a signal when the batteries are low. Wiring shall be permanent and without a disconnecting switch other than is required for overcurrent protection.
1202.16
Smoke Alarm Interconnection.
Where more than one smoke alarm is required to be installed within an individual dwelling unit or sleeping unit in Group R-2, R-3, or R-4, or within an individual sleeping unit in Group R-1, the smoke alarms shall be interconnected in such a manner that the activation of one alarm will activate all of the alarms in the individual unit. The alarm shall be clearly audible in all bedrooms over background noise levels with all intervening doors closed.
Clearly, you could feed the equipment in the main box with 120v. But there is nothing that says you can't step it down to 12 or 16 or 24 volts to go to the alarms. So the 120v. is the Primary power.
And then you have the big battery as back-up.
I do not see the violation. Do I need new glasses?