Has anyone used the Ideal sure test 61-165 circuit anylizer? The one that gives you voltage drop
bighills said:Has anyone used the Ideal sure test 61-165 circuit anylizer? The one that gives you voltage drop
i got the tester and i like it. not quite sure how it checks for voltage drop. every piece of wire i tested with it always shows a vd thats higher than what the nec allows :-?bighills said:Has anyone used the Ideal sure test 61-165 circuit anylizer? The one that gives you voltage drop
The NEC allows almost any voltage drop, but it does have some recommendations.electricalperson said:i got the tester and i like it. not quite sure how it checks for voltage drop. every piece of wire i tested with it always shows a vd thats higher than what the nec allows :-?
peter d said:Testing for voltage drop in a residence is an exercise in futility.
480sparky said:'bootleg' grounds.... that is, grounded receps on ungrounded circuits that have a jumper between the white & green screws.
i installed a receptacle new wire and everything and after i energized it the tester said i had a bootleg ground. i went downstairs and the neutral from the service was touching the can of the panel and i moved the neutral off the can and it was gone.danickstr said:That is a shameful trick.
They will also flasely show a "bootleg ground" if the receptacle under test is sufficiently close to the panel.electricalperson said:i installed a receptacle new wire and everything and after i energized it the tester said i had a bootleg ground. i went downstairs and the neutral from the service was touching the can of the panel and i moved the neutral off the can and it was gone.
electricalperson said:i installed a receptacle new wire and everything and after i energized it the tester said i had a bootleg ground. i went downstairs and the neutral from the service was touching the can of the panel and i moved the neutral off the can and it was gone.
dont know. but when i moved it the false ground went awaymassfd said:Why should this make a diffrence, if it's a service the neutral should be bonded to the can by the bonding screw in the neutral bar
electricalperson said:dont know. but when i moved it the false ground went away
electricalperson said:all this tool is is just a fancy plug tester with a few bells and whistles.
i mean i like the tester but i wouldnt use it to check voltage drop since it doesnt apply a real load just a calculated load somehow.76nemo said:Would you return it if you could get all of your money back?