Quick Question- brain freeze- what rule requires that a 3 phase circuits have color or tap to identify which phase is which? This this apply to apply 3 phase circuits or just that terminating to 3 phase equipment?
IIRC the only requirement for ID is if there is a high leg, and also if there is another voltage system in the building. For the latter, I don't remember if that applies only if the two system conductors share a raceway or enclosure.
We used to use red, yellow and blue with black as the neutral. Now we have the EU "harmonised" colours. Brown, black and grey with blue as the neutral.
Insane.
... what rule requires that a 3 phase circuits have color or tap to identify which phase is which? This this apply to apply 3 phase circuits or just that terminating to 3 phase equipment?
IIRC the only requirement for ID is if there is a high leg, ....
408.3.E.1 Phase arrangement - ABC, and B phase for 4w, 3ph, delta
408.3.F.1 High leg identification
110.15 High leg marking - Orange
Insane.
I know, said it before I'll say it again: worst mistake ever :sick:
Thank you for the code sections!
You probably thinking of 210.5(C)(1) for branch circuits and 215.12(C)(1) for feeders. Both are similarly worded, but really only apply when there is more than one voltage system present on the premises. I don't find similar requirement in art 230 for services.