Re: identifacation
Conductor code requirements were removed about 1975. The CMP has rejected all proposals for conductor color code requirements, as they want you to test and know what the voltage is, and not assume a brown is 277V. The 2002 NEC does require you to post the colors used if two or more nominal voltage systems are used in a facility, see 210.4 (D)
"(D) Identification of Ungrounded Conductors. Where more than one nominal voltage system exists in a building, each ungrounded conductor of a multiwire branch circuit, where accessible, shall be identified by phase and system. This means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means and shall be permanently posted at each branch-circuit panelboard."
A proposal has been made for the 2005 NEC to require some type of identification for all branch ciruits. If you are in favor of this type of color identifcation, you should make a comment on the proposal to the NFPA.
Keep in mind Brown Orange Yellow for 480/277 is fine, as long as you can control the installation by strict specifications and inspection.