Per 200.6 A the grounded conductor #6 and Smaller must be continous white or grey. Per 250.119A grounding conductors larger than #6 are allowed to be marked at the time of installation. Therfore, the neutral (grounded) or equipment bond(grounding conductor) #6 or smaller will need to be continously marked or factory color coded according. My question is how about the ungrounded conductors #6 and smaller. 210.5 does not specify a size limitation, however, local inspectors are requiring all #6 and smaller to be factory colored. This is not usally a problem with #10 and smaller but #8 and #6 is not always stocked a supply houses in colors especially XHHW or is on the job.
Is it a code requirement to mark the entire length of #6 and smaller ungrounded or phase conductors? Is phasing tape acceptable?