Identification of Emergency Circuits- Health Care

Status
Not open for further replies.

emahler

Senior Member
Had an inspector tell me today that in 517, there is an article requiring that all receptacles feed from an emergency circuit (in this case off a generator) need to be labeled with the Panel and Ckt #....

this project is under the '05 code and the nearest thing I could find was 517.30(E)...this site isn't a hospital, it's a dialysis clinic

I didn't dig into it with him today, but i will at the contractors meeting tomorrow night...so long as I'm correct that is:wink:
 
517.19(a). This probably wouldn't apply to a dialysis clinic, but it might be a battle not worth fighting. The staff would probably appreaciate having the receptacles labeled anyway.

Steve
 
Thanks...i didn't see that section...

honestly, we'll label them...it's 12 stations and it's a good idea...

however, i'll argue with him just for fun:D
 