Identification of the "Wild Leg"
Can anybody tell me where this is located in the code??? Thanks in adavance!!
Can anybody tell me where this is located in the code??? Thanks in adavance!!
Q10. I've been looking in the National Electric Code for hours. Does the NEC have any specific reference to wire color-coding for the phase conductors for a 3-phase wye system where the voltage between phases is 480 volts and the voltage to ground from each ungrounded conductor is 277 volts?
A. Yes and No. The NEC requires grounded (neutral) conductors to be white or gray [200-6], grounding conductors to be green or bare [250-119], and the high-leg conductor from a 120/240 volt, 3-phase delta system must be durably and permanently marked by an outer finish that is orange in color [384-3(e)].
Author?s Comment: The reason the high-leg conductor must be identified is because the voltage from this conductor to ground is 208 volts (120 volts x 1.732). Even with the identification of the high-leg, it is not uncommon for the installer to inadvertently connect 120 volt loads to this 208 volt to ground terminal within the panelboard, with unfortunate results (I did it once).
Where more than one nominal voltage system exists in a building such as 480/277 and 208/120, each ungrounded conductor of a multiwire branch circuit, where accessible, shall be identified by phase and system by separate color coding, marking tape, tagging, or other approved means [210-4(d)].
This is something that the NEC should require. The code does not directly prohibit the use of orange for other conductors when you have a high leg system.If red or orange is used to mark the phase having the higher voltage to ground, red or orange shall not be used to mark any other phases.
Don, I am not sure I agree with you. At every point where the conductors are accessible and the grounded conductor is available, the marking must be done.This is something that the NEC should require. The code does not directly prohibit the use of orange for other conductors when you have a high leg system.
Originally posted by tom baker:
Note the high leg only needs to be identified at every accessbile point where the grounded condctor is also present, see 110.15, but Dons comment is correct, I believe it should be identified at every point.
Note the code sections cited by awwt are from the 1999 NEC and some may of changed for the 2002 NEC
Righto. I just wanted to give the OP something to chew on. The discussion was the interesting part to me-- short of the current citations.Originally posted by tom baker:
<snip>Note the code sections cited by awwt are from the 1999 NEC and some may of changed for the 2002 NEC