Identification of the "Wild Leg"
G
Guest
Guest
Re: Identification of the "Wild Leg"
Synonyms:
Stinger.
High-leg.
Mark with Orange.
Here's what Mike Holt said a while back in his newsletter:
Q10. I've been looking in the National Electric Code for hours. Does the NEC have any specific reference to wire color-coding for the phase conductors for a 3-phase wye system where the voltage between phases is 480 volts and the voltage to ground from each ungrounded conductor is 277 volts?
A. Yes and No. The NEC requires grounded (neutral) conductors to be white or gray [200-6], grounding conductors to be green or bare [250-119], and the high-leg conductor from a 120/240 volt, 3-phase delta system must be durably and permanently marked by an outer finish that is orange in color [384-3(e)].
Author?s Comment: The reason the high-leg conductor must be identified is because the voltage from this conductor to ground is 208 volts (120 volts x 1.732). Even with the identification of the high-leg, it is not uncommon for the installer to inadvertently connect 120 volt loads to this 208 volt to ground terminal within the panelboard, with unfortunate results (I did it once).
Where more than one nominal voltage system exists in a building such as 480/277 and 208/120, each ungrounded conductor of a multiwire branch circuit, where accessible, shall be identified by phase and system by separate color coding, marking tape, tagging, or other approved means [210-4(d)].
[ September 17, 2003, 10:40 PM: Message edited by: awwt ]
curt swartz
Electrical Contractor - San Jose, CA
San Jose, CA
As a side note. San Francisco doesn't permit orange for identification or the high leg, they require it to be purple.
I am a "New" Nevada resident(clark county) and I am being told it has to be marked "Orange and Purple" Any one else that can back this up??
Thanks...
charlie
Indianapolis
I wasn't going to jump in on this one. However, you need to reread the various sections that deal with this issue. The high phase, wild leg, etc. is to be marked with orange or other effective means.
Ask any of our linemen and they will tell you to identify it with red. As a result of this long standing tradition, the following was added to the Goldbook, "On a three phase, four wire, delta service, the phase conductor having the higher voltage to ground shall be permanently marked at each point of connection, in accordance with the Indiana Electrical Code. If red or orange is used to mark the phase having the higher voltage to ground, red or orange shall not be used to mark any other phases."
The bottom line is that whatever method is used in your area is OK as long as everyone knows how it is marked and it is permanent. :D
don_resqcapt19
Illinois
retired electrician
Charlie,
This is something that the NEC should require. The code does not directly prohibit the use of orange for other conductors when you have a high leg system.
Don
charlie
Indianapolis
Don, I am not sure I agree with you. At every point where the conductors are accessible and the grounded conductor is available, the marking must be done.
If it is common and acceptable in your area to use blue with red and white polka dots for the high leg, why couldn't another phase conductor be marked with orange? :)
joe tedesco
"Orange" is a color that must be used to identify a certain voltage, and system as per 424.35 and 517.160.
I think there may be a proposal related to the subject of this thread for the "HIGH LEG" using code language found in the Index.
charlie
Indianapolis
Joe, I don't think your references apply since you are talking about heating leads (general wiring is definitely not leads to anything) or an isolated system in a health care facility (you would not mix a circuit that has a grounded conductor with an isolated circuit). :roll:
don_resqcapt19
Illinois
retired electrician
Charlie,
Yes the high leg must be identified with orange or other effective means at every accessible point, but the code does not prevent me from using orange or the other effective means for other conductors in the same building.
Don
joe tedesco
charlie:
Please review the NEC Index for homework, under the following and supply the COLORS used:
Color code
Branch circuits, 210.4(D), 210.5
Conductors, 310.12, 504.80(C), 647.4(C)
Grounded conductor, 200.6
Grounding conductor, 250.119, 310.12(B), 400.23
Heating cables, 424.35
Higher voltage to ground, Feeders, 215.8
Panel boards, 408.3(E)
Sensitive electronic equipment, 647.4(C)
Service-entrance conductors, 230.56
PS: Just trying to teach the new kids on the block about the subject of the color codes used in other areas, and not just in "ancient" electrical systems.
bennie
Esteemed Member
Generally an orange colored phase is B phase on a 480 volt system. There is no wild leg on a 480 volt system.
When the B phase is colored orange on a 240 volt system it is the wild leg.
I don't see any confusion with the identification procedure. I always verify the status anyway.
tom baker
Bremerton, Washington
Master Electrician
Note the high leg only needs to be identified at every accessbile point where the grounded condctor is also present, see 110.15.
Note the code sections cited by awwt are from the 1999 NEC and some may of changed for the 2002 NEC
tom baker
Master Electrician
Originally posted by tom baker:
Note the high leg only needs to be identified at every accessbile point where the grounded condctor is also present, see 110.15, but Dons comment is correct, I believe it should be identified at every point.
G
Guest
Guest
<snip>Note the code sections cited by awwt are from the 1999 NEC and some may of changed for the 2002 NEC
Righto. I just wanted to give the OP something to chew on. The discussion was the interesting part to me-- short of the current citations.
Thanks to all for the updated citations.
[ September 18, 2003, 04:32 PM: Message edited by: awwt ]