Hey there! I am new to the electrical trade and am helping out with the installation of an off-grid PV system with propane generator back-up. My questions are about grounding and bonding of the new system.
First a little background: this system is in a small garage building with attached office way out in the middle of nowhere. It had utility service at one point which fed a 125 Amp panel with only a few branch circuits for lighting and outlets. The utility power was wiped out by floods about 15 years ago, and since then the building has only been powered as-needed by a portable generator. The service conductors have been removed from the panel/service entrance, and there is no possibility of interaction with the grid for the foreseeable future.
We installed a 1.6 kW PV array with a 4.4 kW inverter and battery bank which connects directly to the main panel to feed the premises wiring. Now a generator (12 kW) has been installed behind the building. It feeds a small panel on the back of the building through a 50 Amp breaker. A branch circuit of this panel feeds the inverter (which has AC transfer capability built-in), which subsequently feeds the building loads. The generator is not a separately derived system as the inverter switching mechanism does not interrupt the neutral conductor.
The original panel in the building was grounded through a ground rod placed next to the service entrance, and had a system bonding jumper in place, as one would expect.
My questions are:
1. Since the original "main" panel in the building is now fed by the "generator panel", is it now to be considered and treated as a sub-panel?
2. If so, then shouldn't the bonding jumper be lifted and the neutral grounded at the generator panel instead?
3. Is the grounding electrode system required to be connected directly to the "Main" panel? In other words, can we use the existing ground rod at the sub-panel or does this need to be removed and a new (set) of rods driven at the generator panel?
There has been some considerable debate about this, so I am trying to get an answer that is actually based on code...
First a little background: this system is in a small garage building with attached office way out in the middle of nowhere. It had utility service at one point which fed a 125 Amp panel with only a few branch circuits for lighting and outlets. The utility power was wiped out by floods about 15 years ago, and since then the building has only been powered as-needed by a portable generator. The service conductors have been removed from the panel/service entrance, and there is no possibility of interaction with the grid for the foreseeable future.
We installed a 1.6 kW PV array with a 4.4 kW inverter and battery bank which connects directly to the main panel to feed the premises wiring. Now a generator (12 kW) has been installed behind the building. It feeds a small panel on the back of the building through a 50 Amp breaker. A branch circuit of this panel feeds the inverter (which has AC transfer capability built-in), which subsequently feeds the building loads. The generator is not a separately derived system as the inverter switching mechanism does not interrupt the neutral conductor.
The original panel in the building was grounded through a ground rod placed next to the service entrance, and had a system bonding jumper in place, as one would expect.
My questions are:
1. Since the original "main" panel in the building is now fed by the "generator panel", is it now to be considered and treated as a sub-panel?
2. If so, then shouldn't the bonding jumper be lifted and the neutral grounded at the generator panel instead?
3. Is the grounding electrode system required to be connected directly to the "Main" panel? In other words, can we use the existing ground rod at the sub-panel or does this need to be removed and a new (set) of rods driven at the generator panel?
There has been some considerable debate about this, so I am trying to get an answer that is actually based on code...