mshields
Senior Member
- Location
- Boston, MA
At least one major hospital that we do work in, requires that their IDF rooms utilize the Equipment Branch for the receptacles that are on the generator; including the one that feeds the UPS via an NEMA L14-30. On another hospital I am working on, and this happens to be an IDF associated with an ICU, I followed suite with this and am being challenged that these should be on the Critical Branch. The ammo they are using is the indeed Communications Rooms are listed (paragragh (7) in 517.34, the section listing what should go on the Critical Branch. But a) this is under a paragragh that limits the items that follow it to select receptacles related to patient care. So, now I don't know. What do you think?