jakeparsons03
Member
- Location
- USA
- Occupation
- Engineer
It seems like all Motor Protection Circuit Breakers have a fixed standard magnetic trip of 14x the rated current. From what I have gathered that is the IEC rating for instantaneous circuit breakers (I can't get my hands on a copy of the IEC). However the NEC here in north america has a maximum of 800% rating according to UL Table 31.1 and the NEC table 430.52(C)(1).
With how ubiquitous the Allen Bradley 140xx series is here in the US, there has to be something I am missing on the legality to use these. The only way I could see them being used is on Design B premium efficiency motors according to 430.52(C)(3)(b)(2)(b), where the max is 1700%. What am I missing here?
With how ubiquitous the Allen Bradley 140xx series is here in the US, there has to be something I am missing on the legality to use these. The only way I could see them being used is on Design B premium efficiency motors according to 430.52(C)(3)(b)(2)(b), where the max is 1700%. What am I missing here?