If I connect 12 units of IQ8A microinverters in a single branch circuit?

viji

Member
Location
India
Occupation
Electrical Engineer
IQ8A microinverters allow for a maximum of 11 modules in a single branch if I connect 12 units of IQ8A microinverters in a single branch circuit.

In the future, what problems might I encounter?

But the note indicated that "it may vary based on local requirements" in the datasheet.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
12awg Q cable insulation might melt.
20A breaker might trip.

Since there are saftey factors built in most likely nothing would actually happen. But the above is possible, especially in really high ambient temps or if there's any issues with installation at splices and terminations.
 