Lee Graves
Member
I'm working on a project that involves the use of excessive isolated grounds. The notes on the plans say "the equipment ground and the isolated ground must only be connected / bonded at the service entrance grounding electrode". I've recently been studying grounding through the use of your DVD's and website and came across this information on your site:
"The isolated grounding terminal and the equipment ground would terminate on the same ground bus in your panel. The NEC requires the isolated ground to terminate at the "applicable derived system or service" 250-146(d). Since the panel is fed from a step down transformer, it is a separately derived service, and the grounded conductor (neutral), grounding electrode conductor and equipment grounds are all terminated together, in accordance with Section 250-30."
I have a problem with this statement. According to the Article 100 definition of "service", a service is "the conductors and equipment for delivering electric energy from the serving utility to the wiring system of the premises served". According to this definition, a step down transformer does not create a separately derived 'service', rather a separately derived system.
Question 1: This would lead me to belive that you can terminate the IG conductors at the transformer load side disconnecting means or at the service disconnect?
Question 2: Assuming you can terminate the IG conductors at the service disconnect which will normally be outside, can you also terminate them at the main distribution panel indoors?
Question 3: It seems to make sense to terminate the IG conductors at the transformer, because that would be the source the fault current is trying to return to, correct?
Question 4: If we terminate them at the service, would it essential create a longer fault current path back to the source (transformer)?
Question 5: If the purpose of the IG conductors are to reduce "noise", which location will accomplish this the best?
Question 6: If we run an IG conductor from the panel where the branch circuit originates, all the way back to the building grounding electrode like it specifies in the plan notes, would this conducter be sized according to 250-66 even though it won't be traveling with service coductors? Or do we size it #4 if we're going to a concrete encased electrode?
Question 7: Can we use the same grounding electrode conductor to "loop" between all the panels with an IG bar assuming they all orginate from the same separately derived sourcE?
Any comments will be appreciated. Thanks,
Lee Graves
Lighthouse Electrical Contractors, Inc.
Jacksonville, FL USA
"The isolated grounding terminal and the equipment ground would terminate on the same ground bus in your panel. The NEC requires the isolated ground to terminate at the "applicable derived system or service" 250-146(d). Since the panel is fed from a step down transformer, it is a separately derived service, and the grounded conductor (neutral), grounding electrode conductor and equipment grounds are all terminated together, in accordance with Section 250-30."
I have a problem with this statement. According to the Article 100 definition of "service", a service is "the conductors and equipment for delivering electric energy from the serving utility to the wiring system of the premises served". According to this definition, a step down transformer does not create a separately derived 'service', rather a separately derived system.
Question 1: This would lead me to belive that you can terminate the IG conductors at the transformer load side disconnecting means or at the service disconnect?
Question 2: Assuming you can terminate the IG conductors at the service disconnect which will normally be outside, can you also terminate them at the main distribution panel indoors?
Question 3: It seems to make sense to terminate the IG conductors at the transformer, because that would be the source the fault current is trying to return to, correct?
Question 4: If we terminate them at the service, would it essential create a longer fault current path back to the source (transformer)?
Question 5: If the purpose of the IG conductors are to reduce "noise", which location will accomplish this the best?
Question 6: If we run an IG conductor from the panel where the branch circuit originates, all the way back to the building grounding electrode like it specifies in the plan notes, would this conducter be sized according to 250-66 even though it won't be traveling with service coductors? Or do we size it #4 if we're going to a concrete encased electrode?
Question 7: Can we use the same grounding electrode conductor to "loop" between all the panels with an IG bar assuming they all orginate from the same separately derived sourcE?
Any comments will be appreciated. Thanks,
Lee Graves
Lighthouse Electrical Contractors, Inc.
Jacksonville, FL USA