Sarge590
Member
- Location
- Muskegon, MI
- Occupation
- Manager
Hi All, new to this forum and I could use some help. I work in a large building that has a 3ph 480 delta system coming in. We had a new tenant come in with CNC machines etc. Electrician came in ran all his machines and we have not powered anything up yet. Our power leg to leg reads 480 ish although when we test phase to ground 2 are at 480 and one is at 12V to ground. None of the 3 phase units in the building were having issues but we didn't know why the one leg was reading 12V to ground, I isolated the problem by shutting down all main disconnects to different areas and traced it down to a roof top heater/ac unit, when I shut that disconnect going to the roof top unit that phase now reads 480 to ground and all phases read 480 to ground. Does anyone have an ideas what could cause this? I really appreciate anyone's thoughts on this. Thank you in advance.