Can I supply a Square D Iline panel or a NF panel with 400Y/230 Volts from a 400 volt transformer?

The Iline product description specifically lists 480Y/277V and 208Y/120V, but not 400/230V.
 
Typically the 208/120V panels are rated for up to 250V, and the 480/277V panels are rated for up to 600V
 
I'd be sure to label that panel with big bold stickers indicating that voltage should you decide to do so.

JAP>
 
I would assume they are listed for a maximum voltage also, but the product specs does list all the various US configurations which makes me wonder if anything else (400V) is allowed. I wonder what they do overseas? Someone has to make panels for 400 volts.

Good point about the labels.
 