SC-Retired>NEC-CMP
Member
- Location
- Los Angeles, California, USA
Powering a medium-base lamp socket with more than 120 volts is a violation of the NEC - 210.6. It is dangerous because following persons will screw in a 120 volt bulb "knowing" that the socket is 120 volt supplied - BOOM. The rating of the socket itself does not matter - the application does. The key is the medium-base.
A light fixture that was 277 volt rated due to its being a ballasted type DOES NOT allow the socket to be legally converted to direct supply from the 277 volt circuit.
UL certifying medium-base bulbs at more than 120 volt is a dangerous mistake - it is not a legal NEC installation, and it is dangerous.
A light fixture that was 277 volt rated due to its being a ballasted type DOES NOT allow the socket to be legally converted to direct supply from the 277 volt circuit.
UL certifying medium-base bulbs at more than 120 volt is a dangerous mistake - it is not a legal NEC installation, and it is dangerous.