110.26(D) Illumination. Illumination shall be provided for all
working spaces about service equipment, switchboards,
switchgear, panelboards, or motor control centers installed in-
doors and shall not be controlled by automatic means only.
Additional lighting outlets shall not be required where the
work space is illuminated by an adjacent light source or as
permitted by 210.70(A)(1), Exception No. 1, for switched re-
ceptacles.
110.26(D) doesn't seem to differentiate between indoor and outdoor.
110.26(D) Illumination. Illumination shall be provided for all
working spaces about service equipment, switchboards,
switchgear, panelboards, or motor control centers installed in-
doors and shall not be controlled by automatic means only.
Additional lighting outlets shall not be required where the
work space is illuminated by an adjacent light source or as
permitted by 210.70(A)(1), Exception No. 1, for switched re-
ceptacles.
am I misreading ?
110.26(D) Illumination. Illumination shall be provided for all
working spaces about service equipment, switchboards,
switchgear, panelboards, or motor control centers installed in-
doors and shall not be controlled by automatic means only.
Additional lighting outlets shall not be required where the
work space is illuminated by an adjacent light source or as
permitted by 210.70(A)(1), Exception No. 1, for switched re-
ceptacles.
am I misreading ?
No my error. I read it quickly and thought that the indoors was only for MCC's. :ashamed1:
We need an English major. You may be right. I can read it either way.
I think the word OR may well be saying all the others (anywhere) OR MCCs inside.
Make little sense that way but I can certainly read it that way. Help!, English majors!![]()
We need an English major.
Help!, English majors!![]()
Help!, English majors!![]()
At MacDonald's asking if you want fries with that
I believe that is what the language actually says. The words "installed indoors" only attach to the words "motor control centers".No my error. I read it quickly and thought that the indoors was only for MCC's. :ashamed1:
Local AHJ may have better answers.Is there a NEC requirement for illumination of outdoor gear < 600v ?
I believe that is what the language actually says. The words "installed indoors" only attach to the words "motor control centers".
Local AHJ may have better answers.
Sent from my SM-G935U using Tapatalk
The English language is ambiguous on this point. The scope of the phrase "installed indoors" is undefined in that sentence.I believe that is what the language actually says. The words "installed indoors" only attach to the words "motor control centers".
The English language is ambiguous on this point. The scope of the phrase "installed indoors" is undefined in that sentence.
Cheers, Wayne
Not a problem, the lighting requirement applies to all locations for the other equipment, both indoor and outdoor.Then isn’t there a big problem. What applies to other electrical equipment and rooms indoors?