Hey everyone. I am back with more problems. I was doing good for a while but I have ran into another wall so I thought I would post.
What would be the minimum general lighting demand for a 2000 square foot residence with 2 small appliance branch circuits and a laundry circuit?
a. 10,500 watts
b. 6,000 watts
c. 5,625 watts
d. 3,675 watts
The sample test I am using says that the correct answer is c. I can come up with 6,600 VA but that is as far as I can get. This is how I am coming to that. I do my lighting load calculation 2000 x 3 = 6,000. I turn to Table 220.42 and see that it says From 3,001 to 120,000 use 35% Demand Factor. So I take 6000 x 35% which gives me 2,100. I then turn to section 220.52 sections A and B. That gives me 4,500. I add that to my previous 2,100. 4,500 + 2,100 = 6,600 VA.
What am I doing wrong. I am using NEC 2011. Thanks for all the help.
What would be the minimum general lighting demand for a 2000 square foot residence with 2 small appliance branch circuits and a laundry circuit?
a. 10,500 watts
b. 6,000 watts
c. 5,625 watts
d. 3,675 watts
The sample test I am using says that the correct answer is c. I can come up with 6,600 VA but that is as far as I can get. This is how I am coming to that. I do my lighting load calculation 2000 x 3 = 6,000. I turn to Table 220.42 and see that it says From 3,001 to 120,000 use 35% Demand Factor. So I take 6000 x 35% which gives me 2,100. I then turn to section 220.52 sections A and B. That gives me 4,500. I add that to my previous 2,100. 4,500 + 2,100 = 6,600 VA.