MichaelGP3
Senior Member
- Location
- San Francisco bay area
- Occupation
- Fire Alarm Technician
I ran into something today I can't explain. Transformer (120V to 24V) in its own integral housing installed on the top of a NEMA enclosure, wired to this rectifier,
http://www.partsexpress.com/images/050-060m.jpg
installed inside the NEMA enclosure. The 24VDC+ output of this rectifier is wired to the common (aux. contact) terminal in an analog addressable smoke detector base. The N. O. terminal feeds this DC+ voltage (during an alarm condition) to the coil of a 24VDC 2 pole form 'C' interposing relay. The 24V DC- wire goes directly from the rectifier to the coil of the interposing relay, which is used to light a 24VDC incandescent lamp. Wiring is THHN 14 gauge stranded, in 3/4" EMT.
When the wires are removed from the DC output side of the rectifier, they read as free of foreign or induced voltages, shorts, and grounds.
Using a Fluke model 83 VOM, with a clear fire alarm (no off normal conditions) I'm reading the following:
Output side of transformer/input side of rectifier: 25.5 VAC
Output side of rectifier, with field wires not connected: 23 VDC
Output side of rectifier, with field wires connected: 33 VDC
These readings are stable.......any ideas? With no load on the wires, I would have predicted no change in the rectifier's output voltage.
http://www.partsexpress.com/images/050-060m.jpg
installed inside the NEMA enclosure. The 24VDC+ output of this rectifier is wired to the common (aux. contact) terminal in an analog addressable smoke detector base. The N. O. terminal feeds this DC+ voltage (during an alarm condition) to the coil of a 24VDC 2 pole form 'C' interposing relay. The 24V DC- wire goes directly from the rectifier to the coil of the interposing relay, which is used to light a 24VDC incandescent lamp. Wiring is THHN 14 gauge stranded, in 3/4" EMT.
When the wires are removed from the DC output side of the rectifier, they read as free of foreign or induced voltages, shorts, and grounds.
Using a Fluke model 83 VOM, with a clear fire alarm (no off normal conditions) I'm reading the following:
Output side of transformer/input side of rectifier: 25.5 VAC
Output side of rectifier, with field wires not connected: 23 VDC
Output side of rectifier, with field wires connected: 33 VDC
These readings are stable.......any ideas? With no load on the wires, I would have predicted no change in the rectifier's output voltage.