Martin County
New member
I have a contractor with 21 current carrying conductors in a raceway.
The conductors are #12 thwn-2 and are installed on 20 amp breakers.
I have failed this job and cited table 310.15(b)(2)(a). The contractor states that the load on the branch circuit conductors do not exceed the derated values and that this table is not for sizing overcurrent protection. Please advise and reference as soon as possible as I will not release power to this new business. I may be reached by PM
Sincerely:
In the interest of public safety
Mike R.
The conductors are #12 thwn-2 and are installed on 20 amp breakers.
I have failed this job and cited table 310.15(b)(2)(a). The contractor states that the load on the branch circuit conductors do not exceed the derated values and that this table is not for sizing overcurrent protection. Please advise and reference as soon as possible as I will not release power to this new business. I may be reached by PM
Sincerely:
In the interest of public safety
Mike R.