Davebones
Senior Member
- Location
- North Of Tampa Fl
We have a new production room with different immersion tanks . These tanks have ( 21KW , 3 phase , 480v , rated 25.3 amps ) over the side heaters installed . Each heater is on a Eaton FAZ-D30/3 breaker being fed with #10 wire . Each of these breakers ( 6 total ) are very hot . Amperage shows they are drawing 29 to 30 amps each leg . The designer of these control panels is saying check the connections and voltage coming in . We checked the connections all good . The incoming voltage is ( 280,281,283 to ground / 482,488,488 phase to phase ) . Distance from control panel to tanks is only about 40 ft . I feel these need to be on 40 amp circuits even thou the nameplate says they draw 25.3 amps as they're drawing 29 to 30 amps . Any other thoughts on this ?