Impact of high THD-F
SKhaja
Illinois
designer
Greetings Gents,
I have a situation where I had to get a power metering study done at one of the plant facilities for determining load amps at overhead busses connected to a LVS.
This was done to check whether or not the existing MCCB feeding the overhead bus is sufficient. What I discovered was that these busses have a high THD-F content (greater than 14%).
Could someone inform what implications could this have particularly when it comes to the sizing of cables ?
Thanks in advance.
In the US we only have harmonic standards at the utility meter (point of common coupling), so I could refer you to the THD limits of IEEE 519, but that is not fair to compare the limit of the whole service to a particular feeder.
Generally no impact from THD to feeder sizing.
It is similar to PF, in that, THD is like a silent increase to heat in the transformer and other points of coupling. It is more of a nuisance to sensitive electronics than it is a problem at small %s.