ish1284
- Arlington Heights, IL, USA
Hello,
I am well versed in evaluating low voltage molded case circuit breakers against calculated short circuit currents. I understand that if the x/r ratio of the calculated RMS symmetrical current is greater than the breaker's UL text x/r that the breaker must be de-rated based on a multiplication factor per IEEE-242.
I also understand how to calculate this multiplication factor.
What I don't understand is the mechanics. What does a higher x/r ratio do to the circuit breaker. I understand that the higher x/r ratio, the higher dc component, and also the higher peak current. Does this make the breaker harder to interrupt? Does it make the breaker more susceptible to being damaged or melting contacts?
Manufacturers only provide a symmetrical RMS rating for UL listed low voltage circuit breakers and typically do not want to bless off on any values given to them in terms of peak asymmetrical. Is it an absolute must to consider the peak asymmetrical current or is this just recommended practice?
Let's discuss!
Let's discuss!