Re: Impedance calculation
Unless y
our going to wrap those conductors around something a number of times there won't be a significant value of inductive reactance.
Without inductive reactance "impedance" is the same value as the DC resistance.
Based on my tables I get 0.0612 ohms for your conductor run, a little higher if it's aluminum instead of copper.
I think you should be more concerned with temperature and insulation. If you use THHN your conductors will be suitable to carry 75 amps at 194 degrees F. Some other insulations only allow 55 amps at lower temperatures.