Here is the installation. It?s a central plant for a hospital. There are going to be two 1000KVA 4160V generators with provisions for two more in the future. A line up of paralleling gear ties everything together. All overcurrent/disconnecting means are in the paralleling gear. The plans call for neutral grounding resistors for each generator. These will consist of one Avtron N/G resistor for each genset.
250-180 states that high voltage systems shall comply with all applicable provisions of the preceding sections. What I am unclear on is the actual wiring method for the resistors. Does the conductor have to be fully insulated to 5KV? 250-36(d) allows the conductor to be run in its own raceway. Does this apply to >1000V systems too?
If I am interpreting this right I can run the grounding electrode conductor to ground the gensets into the paralleling gear and make all the grounding connections there. Then run a (600V or 5KV?) insulated conductor in a conduit to the NGR. From there that conductor can continue to the genset in its own conduit to the neutral point of the generator. The 5KV circuit conductors would then run from the paralleling gear to each generator without an equipment grounding conductor. (If one were run it would effectively shunt the resistor) IS this correct?
I tend to want to run two conductors to the N/G resistor in the same conduit. One from the equipment ground bus to the resistor, one back to the gear to run back with the 5KV circuit conductors. Does anyone have some experience with this?
250-180 states that high voltage systems shall comply with all applicable provisions of the preceding sections. What I am unclear on is the actual wiring method for the resistors. Does the conductor have to be fully insulated to 5KV? 250-36(d) allows the conductor to be run in its own raceway. Does this apply to >1000V systems too?
If I am interpreting this right I can run the grounding electrode conductor to ground the gensets into the paralleling gear and make all the grounding connections there. Then run a (600V or 5KV?) insulated conductor in a conduit to the NGR. From there that conductor can continue to the genset in its own conduit to the neutral point of the generator. The 5KV circuit conductors would then run from the paralleling gear to each generator without an equipment grounding conductor. (If one were run it would effectively shunt the resistor) IS this correct?
I tend to want to run two conductors to the N/G resistor in the same conduit. One from the equipment ground bus to the resistor, one back to the gear to run back with the 5KV circuit conductors. Does anyone have some experience with this?