I need a fan to cool an enclosure located in a Class 1 Division 2 rated area. I've found a fan that is "self-certified" by the manufacturer for C1D2 use by virtue of NEC 501.8-B because the motor is "impedance protected". I do not see any reference to "impedance protected" in that section of the NEC. Since no agency (UL, CSA, FM) has tested and approved the fan, I am skeptical. Is an impedance protected motor acceptable for use in a Class 1 Division 2 area?
charlie
Indianapolis
Re: Impedance protected motor in C1D2 area
It is if the AHJ approves the installation. If I were the AHJ, I would ask for a field evaluation from a NRTL. :D
don_resqcapt19
Illinois
retired electrician
As long as the motor does not have arc producing contacts, no special listing is required for Class 1, Division 2 locations.
501.8(B)... In Class I, Division 2 locations, the installation of open or nonexplosionproof enclosed motors, such as squirrel-cage induction motors without brushes, switching mechanisms, or similar arc-producing devices that are not identified for use in a Class I, Division 2 location, shall be permitted.
Don
charlie
Indianapolis
OOOPS, so much for being so sure of your answer that you don't look it up. It is not good to shoot from the lip. :eek: